  • #36627

    suenpaul
    Member

    Just had a Baxi Luna HT380 installed and we are getting an error code E119 – No water pressure. Yet the pressure is 1.25 Bars and in the acceptable range. Any ideas on how to bypass this?

    Thanks, Paul

    #40992

    farrukh_najmi
    Participant

    I have the same problem this morning. However my water pressure reading is in the 0 (red) range. Anyone have any idea how to fix this? Thanks.

    #40996

    farrukh_najmi
    Participant

    I had E119 recently. We had no hot water and water pressure was 0!

    It turned out that the valve at the top of the pressure tank was stuck. By flipping it up briefly I was able to get the water pressure restored to 1.5 psi and the error code was cleared. We now have hot water!

Viewing 3 posts - 1 through 3 (of 3 total)