#66910
gordo
Participant

on lower end/ copy type gen sets the power modual is usually the issue. just inside the cover for the gen there will be a small flat(about 3 1/2 in by 1 1/2 in ) electric control between the gen output and the outlet input.

you can just disconect and see if power is coming off the leeds from the gen(if no power its your coil) if there is power the check continuity between the leeds on each side.

what this unit does is the same as a charge controler. it keeps the power consitant to the outlet.

the part if availible are about 150 bucks.

good luck

gordo